HARTONO Zainal Abidin, BSc, MIEEE and ROBIAH Ibrahim, BSc, MIEEE
The lightning protection systems (LPS) used in this country and around the world is basically divided into two types:
The recognized lightning protection standards frequently applied in Malaysia are the MS-IEC 61024 (Malaysian/IEC), BS6651 (United Kingdom), NFPA780 (USA), AS/NZS 1768 (Australia/New Zealand), and CP33 (Singapore). These standards are regularly updated to incorporate the new findings on lightning protection researches.
In addition to the above, the vendors of the unconventional LPS have introduced/proposed their own ¡°product standards¡± such as the French NFC 17-102. These so-called ¡°standards¡± have already been rejected by the scientific organizations in their country of origin.
Work to revise this standard commenced in the late 1990s and the new interim standard, AS/NZS 1768(Int) 2003, was published in December 2003. The existing methods for positioning the air terminals, namely the Protection Angle Method (PAM), the Rolling Sphere Method (RSM) and the Faraday Cage Method (FCM), are still retained.
The standard also incorporates a new air terminal positioning method that is based on observations of lightning induced damages in Malaysia. The description of this new method is as follows:
¡°Field data of damage caused by lightning flashes terminating on structures (See Appendix G, Refs 2 & 3) identify the parts that are vulnerable to strikes. The most vulnerable, associated with
over 90% of observed lightning damage, are nearly always located on upper parts of structure, such as:
Work on the revised standard commenced in the late 1990s and it was finally published in February 2006 to replace the IEC 61024. The new standard is divided into four parts:
This ¡°standard¡± was published in 1995 by GIMELEC, the association of French ESE manufacturers, in order to standardize the manufacture, test and installation of the ESE air terminals. The ¡°standard¡± has been copied by other non-French ESE manufacturers e.g. Spain.
The NFC 17-102 was criticized in 2002 in a report [1] by the French scientific agency, INERIS, for non-implementation by the ESE manufacturers. Although the manufacturers have agreed to revise the document, no action has been taken so far. Hence the ESE air terminals now in use worldwide have not only failed to comply with the recognized national/international standards but they also failed to comply with the manufacturers¡¯ own standard.
Between 1989 and 2005, the inventor of the CTS made five applications to the NFPA to include the CTS in the NFPA780 standard. All the applications were rejected because the inventor could not provide the required scientific theory to support the CTS. The latest rejection [2] was made by the NFPA in 2005.
The CVM is a proprietary method for positioning the Dynasphere¢ç air terminal, an active air terminal developed in Australia. This method was included in the appendix of the AS/NZS 1768:1991 for information only. However, it was applied in many countries for the installation of the Dynasphere ¢ç air terminals. The CVM was also re-named as the Field Intensification Method (FIM) in 2002.
Field data collected in Malaysia over ten years on the application of the CVM/FIM failed to prove that the method is valid for air terminal positioning since most of the buildings that used the method had been struck and damaged by lightning. Consequently, the CVM/FIM was deleted from the AS/NZS 1768(Int):2003.
The CVM/FIM was also rejected by the NFPA [3] in 2004 for the same reasons.
Following the rejection of the ESE technology by the NFPA in 2000, several American ESE vendors brought the matter to court alleging ¡°unfair trading practices¡± on the part of their opponents. However, after lightning experts were called in to testify on the workings of the ESE technology, the court issued a judgement [4] prohibiting the ESE vendors from claiming that their product can provide a protection zone that is much bigger than that of the Franklin rod. The court had decided that the claims made by the ESE vendors constituted false advertising and violated the US Lanham Act.
In September 2005, the ICLP issued a warning [5] that the use of the unconventional LPS posed a danger to the end user and general public. The warning highlighted the studies of ESE air terminal failures under real lightning conditions conducted in the USA and Malaysia. Following this warning, ACEM had issued an advisory (Ref: ACEM/sec/2005/13 dated October 27, 2005) to all its members to stop using the unconventional LPS.
The following cases highlight the recent failures of the ESE air terminals in Malaysia:
The ESE air terminals are being used by some home developers to protect detached houses and low rise apartment blocks. However, the cases below show that the claimed enhanced zone of protection of the ESE air terminals had failed to prevent lightning from striking these buildings, either singular or in a cluster.
Case 1: Cluster application failure
The minaret of the mosque, completed in 1998, is a slim 116 m high structure that was installed with a single ESE air terminal on the apex. According to the RSM, the sides of the minaret from about 50 m and above are exposed to lightning strikes and require protection.
The protection provided by the ESE air terminal, according to the NFC 17-102 ¡°standard¡±, should be at its best since the diameter of the minaret is less than 10 m. However, in 2005, lightning struck the side of the minaret about 30 m below the apex. This clearly shows that the claimed enhanced zone of protection for the ESE air terminal is non-existent.
This large building has been installed with at least five ESE air terminals, one on the apex of the dome and four on ridge ends of the metal roofs below the dome. A photograph of a lightning strike to the dome air terminal was recently captured by a news photographer.
An analysis of the lightning path that terminated on the air terminal shows that the ESE principle is incorrect. If it was correct, then the lightning path would be approximately straight for several tens of meters above air terminal since the streamer would be moving towards the down leader.
The curved path of the lightning stroke just above the air terminal indicates that no streamer was emitted. In addition, no visible streamers were observed from the nearby ESE air terminals on the metal roofs. As already shown in the previous report, a corner of the building next to one of the lower ESE air terminals had been struck by lightning.
Studies in support of the CTS and ESE technologies were made by University of Technology Malaysia (UTM) researchers since 2003. Although they claimed to have found the proof for these technologies, the findings were still inconclusive.
These studies were made jointly with researchers from Telekom Malaysia Research and Development. The studies by Ramli and Ahmad [6],[7] claimed to have validated the CTS technology based on data obtained from the Malaysian lightning detection network (LDN), lightning video recordings and lightning current measurements made on the CTS air terminals. However, it was found that the erroneous conclusions were made based on misinterpretation of all the three data [8].
These studies were conducted at the university¡¯s high voltage institute, IVAT.
In a study by Ngu and Darus [9], the ESE technology was validated based on observed field data which consist of the number of observed lightning strike damages and selected lightning counter readings. However, the data in this study were found to be similar to the CVM/FIM data submitted by an ESE vendor to Standards Australia. Since the CVM/FIM has been rejected by Standards Australia and the NFPA, the validity of this study is questionable.
In a study by Sidik and Ahmad [10], a new ESE air terminal equipped with a wind-driven electrostatic generator and a palmsized laser device was invented. They claimed [11] that the laser device is capable of attracting lightning strikes and that the air terminal operates on the CVM principle. They also claimed [12] that their invention need not be installed on the building for protection against direct lightning strikes.
Since 2004, no new evidence has been submitted to support the hypotheses behind the unconventional LPS. On the other hand, more evidence has been presented to demonstrate the inefficacy of the unconventional LPS in field applications. The ICLP has issued a warning that the use of the unconventional LPS is dangerous.
The revised national and international lightning protection standards have also included a new air terminal positioning method that will significantly improve the protection of buildings from direct lightning strikes.
Studies conducted by local research institutions in support of the unconventional LPS have also been shown to be inconclusive while a new ESE air terminal developed by a local university is based on discredited and unproven technologies.
The authors wish to thank The Star Publications PLC for permission to use their award winning photograph of the lightning strike to the Prime Minister Department building.
The authors of this paper have been conducting forensic analyses on lightning damaged electronic systems since 1980 and have been conducting research on the effects of lightning strikes to buildings since 1990. They have published over two dozen scientific papers on these subjects in local and foreign conferences and journals. Their research works is highly cited in western scientific journals since 1995 and have been included in the revised Australian and IEC lightning protection standards.